PanelView Plus will not talk to a 5069-L306ER after a v37 flash

Allen-BradleyField note

The question

CompactLogix 5069-L306ER at rev 37. PanelView Plus 7 2711P-T12 still on an older firmware. FactoryTalk shortcut looks right. RSLinx browses both. Runtime on the terminal sits on a red comms banner. Do I flash the terminal first, or is there a fake-controller workaround that still works on v37?

TS ControlsThe answer

Flash the PanelView. v37 CompactLogix wants a current terminal firmware — the old CE image will browse in Linx and still fail at runtime. A 1769-L35E stand-in in the comms path is a lab trick, not a production plan. Copy the shortcut to the Runtime tab, one tag, one screen, prove comms, then bring the real app back.

Replies from members

  1. Loading replies…

Log in to reply. Google, X or email.