1769 analog input — 4–20 reads 3.9 mA after a lightning weekend

Allen-BradleyField note

The question

CompactLogix analog, loop powered transmitter. After a storm every channel sits a hair under 4 mA. Replaced one transmitter, same reading. Card, 24 V, or a shared common that got lifted?

TS ControlsThe answer

Measure 24 V under load at the card, then at the transmitter. Storms lift commons. If all channels are 3.9, it's the supply or the analog common, not every transmitter dying together. Don't rescale in the PLC to make 3.9 look like 4.