The question
L83, EN2T, Windows 11 laptop, Studio 5000 v36. RSLinx Classic browse shows the chassis. Studio path is empty. USB to the processor works. Ethernet is the one that lies. What did you flip that wasn't 'run as admin'?
TS ControlsThe answer
Studio is using FactoryTalk Linx now, not Classic. Point the driver's EtherNet/IP browse at the same subnet and turn off the Wi-Fi NIC. We also had Windows filtering IPv4 on the Ethernet adapter after a VPN client. Classic can still see CIP; Studio will not until FT Linx has a driver that matches.