KUKA interrupt fires twice on the same skip — path jerks, then continues

RoboticsField note

The question

KR QUANTEC, KSS 8.6, interrupt on a skip condition from the PLC. First edge is correct. A second fire 40 ms later jerks the path. DECLARE is in the submit. I thought BRAKE in the interrupt would make it one-shot.

TS ControlsThe answer

Debounce the PLC bit and GLOBAL INTERRUPT DECL once. BRAKE stops the motion; it does not prevent a second trigger if the bit is still bouncing. INTERRUPT OFF in the handler, do the work, INTERRUPT ON when the condition is gone. Watch CYCLE_TIME vs the PLC scan — a 40 ms double is a classic unlatched skip.