The question

Wastewater, Profibus DP, AUMA AC 01.2. After we moved the starter bucket the actuator LCD boots then dies on WD-Timeout. Same address, same GSD. Comms LED on the master looks healthy. Is this a 24 V sag, a termination, or the actuator firmware fighting the new PSU?

TS ControlsThe answer

WD-Timeout on AC 01.2 after a bucket swap is almost always the 24 V coming up slower than the board watchdog. Measure at the actuator, not the panel. If it dips under 21 V at boot, the head never finishes init. We also had a Profibus terminator left OFF on the new bucket. Don't reflash until those two are clean.