Motion in SCL or keep it in ladder so maintenance can still read it?

SiemensField note

The question

S7-1500, two axes, cam table. SCL is cleaner. The night tech reads ladder. If I hide the motion in an FB with a ladder wrapper, is that a peace treaty or a mess?

TS ControlsThe answer

Peace treaty. Motion math in SCL inside an FB. Interlocks, permissives, and the 'why is it stopped' bits in ladder on the face of that FB. Comment the in/out. Night shift should not have to parse a cam polynomial at 2 a.m. They should see the permissive that is false.

Replies from members

  1. Loading replies…

Log in to reply. Google, X or email.

Same fault on your line?

We can come fix it.

Send the platform, the symptom and the outage window. A TS Controls engineer answers with a plan.

Line down Send an RFQ